adminKeymaster
YOU CAN USE SYNCHRONOUS CONDENSERS WHICH ARE EASY TO CONTROL
adminKeymastermajid amoudi said:
voltage drop formula- root3*VI(rcos(fie)+jxsin(fie))*L(where L is in KM).
majid amoudi said:
voltage drop formula- root3*VI(rcos(fie)+jxsin(fie))*L(where L is in KM).
THIS FORMULA DIFFER ACORDING TO LENGTH OF TRANSMISSION LINE: FOR SHORT TRANSMISSION LINE IT IS V (DROP)=Iz Z IS impedance and it is for single phase so, for balance 3-phase it s multiple of three
adminKeymastervoltage drop formula- root3*VI(rcos(fie)+jxsin(fie))*L(where L is in KM).
adminKeymasterHi Jennifer,
Hru?I m searching 4m few days,but didn't get anything about calculation of electrical equipments like busbar,MCB,MCCB n all.
Will u plz do me a favour,will u plz mail me that site n books name with ISBN no.
I m thankful.
adminKeymasterit will give back up for 20 minutes
adminKeymasterwho can tell how to wire a motor
adminKeymasteryes i can
adminKeymasteredil said:
hi…is there anyone could help me in installing a two way separate electrical outlet in one box
take another switch & install it simply.
adminKeymasterHi, rumora
You may be use Dialux Software
adminKeymasterThe input is 35 KW ,3 phase voltage is specified.We ned to calculate resistance of cable conductor /Km & apply the fourmula of
Receiving end Power = sending end power ( 35 KW) – ( power Losses in conductor /cable+ shut capacitence impedence along the O.H.line for 35 Km),Gives you the answer.It will decrese if you use 440 Volts ,if transmit same through 3.3 KV it will increases,as per my little knowledge goes.
adminKeymasterthis information is very informative for all electrical engineer and electric lover, thank you for sharing.
adminKeymasterHi, In situations like this, I would always use a Stainless steel cabinet with Rittal type SK Stainless steel Rain hoods over SK fan / filter units. You will need to work out the airflow for the enclosure based on the heat rejection value from the Variable speed drive you are using.
The rain hoods slide up to gain access to the filter unit for maintenance, this should also stop any salt water spray from entering the enclosure.
Regards
Dave
adminKeymasterAssume
35m cable length
10amps / phase
Cable 10mm² = 0.00343Volts drop per amp per meter from cable manufactures tables) copper
0.00343 x 35m x10 amps = 1.20v drop (at the end of the 35m)
adminKeymasterHave any of you ever heard of a software called Volts? It's made by a company called Dolphin. They're located out in California. It's very handy. It actuallly sizes the electrical system taking every adjustment factor into account. It also creates a one-line diagram.
adminKeymasterThe accuracy of the meter will depend on the size of the CT that was installed. If the CT/s is/are too big in capacity as compared to the power that is actually consumed or the power that is passing through the meter, it will never give a “close to real” measurement.
-