Viewing 15 posts - 451 through 465 (of 508 total)
  • Author
    Posts
  • in reply to: Parallel transformer electrical distribution #11592
    admin
    Keymaster

    Dorin Pestereanu said:

    Hello !
    Wonderfull blog for electrical engineer and for electricians !
    I have a question : Where I can get gratis download soft for Electrical Cad 2004 ?
    Thanks!

    I think in the operation of transformer is severly depend upon the loading of trasformer in distribution system as in msximium loading efficiency of distribution trasformer decreses which is a big  reason for distribution loss parallel operation of trasformer is good solution for that. 

    admin
    Keymaster

    JohnB said:

    “Power factor is that of the load & not of the alternator” is right. In an islanded situation (standalone generation system) , the alternator must supply power at a power level and a power factor dependant on the load. The alternator can’t do anything else. Power factor correction in this instance will improve the load power factor (and hence reduce alternator ine current).

    If however the alternator is operated in parallel with the grid, power factor of the alternator can be changed by changing alternator excitation (assuming it is a synchronous alternator).


     

    As power factor is ratio of active power to apparant power(KW/KVA) AND active power & reactive component is contolled by alternator feed fuel system and excitation control,hence by controlling these two we can control power factor of load and alternator.

    admin
    Keymaster

    “Power factor is that of the load & not of the alternator” is right. In an islanded situation (standalone generation system) , the alternator must supply power at a power level and a power factor dependant on the load. The alternator can’t do anything else. Power factor correction in this instance will improve the load power factor (and hence reduce alternator ine current).

    If however the alternator is operated in parallel with the grid, power factor of the alternator can be changed by changing alternator excitation (assuming it is a synchronous alternator).

    in reply to: KW Calculation #11581
    admin
    Keymaster

    considering distance and size of cable,it is likely to decrease.

    in reply to: Best electrical calculation software review #11586
    admin
    Keymaster

    Dear Laurent your comparison is very interesting, I agree with your classification.

    in reply to: Software for electrical installation #11576
    admin
    Keymaster

    i need a powerfull simulation software for renewable energy/ a

    hybrid system consist of wind, solar, hydropower

    thank you for your advice

     

    admin
    Keymaster

    vilas said:

    akhilesh said:

    if new method u know then plz send msg me.plz…………..dears………

     


     

    Power factor is that of the load & not of the alternator.Therfore there is no question to improve the pf of the altertnator. Off course the power factor at which the alternator is feeding the load can be improved by reducing the RMVA loading of the alternator.


     

    such lame understanding of electrical engineering principles, if not, utterly stupid…. 

    in reply to: distribution transformer #11437
    admin
    Keymaster

    by using step down transformer

    in reply to: distribution transformer #11566
    admin
    Keymaster

    how to make power from 220 v to 12 v?

    in reply to: PUMP POWER CALCULATION #11558
    admin
    Keymaster

    Get the power consumption in KW which shld be on the pump required, the current can be calculated from there.

    in reply to: distribution transformer #11557
    admin
    Keymaster

    Hello wat do u mean find cables do u mean the sizes or availability?

    admin
    Keymaster

    Guys…that are two different things.

     

    example,

    Generator set with 0.8 power factor mean:

    alternator unit will be in kVA with engine unit will be in kW with factor 0.8 (not the alternator)

     

    at the load side, power factor is kW/kVA which is a composite of power factor

    the composite power factor at the load side are possible to be corrected but generator (set) power factor cannot be corrected unless by changing the engine capacity or alternator capacity.

     

    hope the above could helps you

    in reply to: KW Calculation #11555
    admin
    Keymaster

    its increase brcause of resistance of wires that is called  VOLTAGE DROP

    in reply to: PUMP POWER CALCULATION #11553
    admin
    Keymaster

    please i need pump power calculation

    in reply to: Lightning & Surge protection #11552
    admin
    Keymaster

    Hello, tree-phase protection at the building entrance (using heavy discharge tubes made by TTI Puerto Rico) has solved most problems in Venezuela. However there is a ever growing problem present, probably world-wide. The problem is as follows:

    Most computer users buy “stabilyzers” using MOV type surge protectors. These are single-phase devices and see what the happens doring a lighning storm: when surge arrives, the sinle phase MOV will cut the overvoltage surge to a save level for the computer it is ment to protect. But now the catastrophic effect is because the power clippling at one phase rises very dangerously spikes at athe other two phases at the whole building. I have seen a chane of PC failures that did not have MOV protection.

    This effect should be communidated to all computer-users !

    The real solution is really a building-entrance protection, while the individual MOV protection at the consumer load is too danderous !

    Please comment your experience ! Rehards Hans Stauffer, Caracas Venezuela (stauffer@cantv.net)

     

Viewing 15 posts - 451 through 465 (of 508 total)