  • in reply to: Panel builders are all cheaters? #11967
    NV Mani
    Participant

    Panel builders basically assemble components.
    If the components are tailor-made it will take more time to assemble.
    But if components are standardised,to suit commonly for a bigger range of end users,in modular design,
    in cost effective way,time and thus cost can be minimized.

    in reply to: Substation Methodology of installation #11378
    NV Mani
    Participant

    Major steps are listed below:
    A. Design aspects
    (1)Conforming standards,regulations for design are to be identified.
    (2)Arriving at Power demand:plan to import from grid/plan as captive generation
    (3)Service connection: High – Medium – Low Voltage levels.
    (4)Single line diagram of distribution,schematics,Protection and metering.
    (5)Safety and fire protection systems,Lighting,Earthing,Lightning protection.
    (6)Technical specifications and engineering for equipment procurement and installation.
    (7)location of substation,equipment and cable layouts.
    (8)Obtaining statutory approvals and clearances in writing for commencement of work.

    B.Construction and commissioning aspects
    (1) Engage competent consultant for design,engineering,construction,testing and commissioning.
    (2) Preparation of comprehensive tender document,specifying detailed construction standards.
    (3) Awarding construction contract to licensed and competent electrical contractor.
    (4) Release of all construction drawings.
    (4) Ensure strict compliance with quality and safety in work through continuous site supervision.
    (5) Test all installations and conform fitness for commissioning through certified test reports.
    (6) Obtain statutory approvals and clearances in writing for energising electrical systems.
    (7) Ensure all documentation,guarantee runs,training of maintenance and operation staff before making
    final payment to contractors,consultant and equipment suppliers.
    The documentation should include “as built” drawings.
    (8) The spare parts for 2 years trouble free operation shall be kept in stock.

    Wherever,in house capabilities are limited (only on such areas),AMCs shall be finalised for regular maintenance and repairs.

    I might have missed some points which may be added as needed.

    in reply to: Current rating calculation of any kind of motor #11377
    NV Mani
    Participant

    When you say calculate current rating of the motor,it means current drawn by the motor from the mains is to be calculated.
    For this you should know first what is the output rating in HP or KW.
    From this known value of mechanical power output,you can know the electrical power input only by knowing the efficiency of conversion of electrical energy to mechanical energy.
    From the known values of Mechanical power output and efficiency you can calculate the Input electrical energy in KWH.The line voltage for star connection is 1.732 times the phase value.If Power factor value is given,it is known or assumed as 0.8.
    Now the formula,which you know, KWH = Line Current * Line Voltage * Power factor can be applied.
    The only unknown value ‘current’ can be calculated.

    in reply to: Current rating calculation of any kind of motor #11372
    NV Mani
    Participant

    Full load current in amperes = KW (Input power) / 1.732 x Volts(Input voltage)x power factor X efficiency
    (if motor is 3 phase motor)