  • in reply to: Convert single phase to three phase #12285
    s
    Participant

    There is another way, if you can;t modify in internal connections

    you can use a capaitor with the following arrangement

    1- the connection should DELTA

    2- the delta poles are A,B,C

    3- L1 is connected to A, N is connected to B, the capacitor is connected to A and C

     

    this should do the trick

    Regarding the capacitor rating, frankly i don't know the calculations, maybe Mr.Spir (My mentor) can help with this.

    s
    Participant

    Ok, 

    Firstly , out of personal experience I don't recommend messing around with generators unless you have the experience, patience and time,

    Second, how many persons have the access for the generator? is it only you? or there is many people have the access?

     

    Your problem is either electrical or mechanical,

    If it's mechanical that means the generator temperature is at critical levels and the cooling system needs maintenance ( here PLEASE do not do it yourself unless you are qualified ) 

    If it's electrical, that means the temerature sensor is either needs re-adjusment or replacement, also check the control unit settings, there is a big chance (if you are not the only one has the access for generators) that someone messed with control settings,

     

    Anyway, refer to the manual and check if your problem is mentioned there,

     

    Regards

    in reply to: Voltage Addition #12268
    s
    Participant

    if it has terminals of +12 and -12, yes you can

    in reply to: Increased generation of Hydrogen in Transformer #12267
    s
    Participant

    Consult the manufacturer

    s
    Participant

    Power factor concept is applicable on loads not sources

    in reply to: Generation of incresed hidrogen gas in transformer #12265
    s
    Participant

    You should consult the manufacturer

    in reply to: distribution transformer #12264
    s
    Participant

    What are the primary and secondary voltages of this transformer?

    in reply to: Power Quality #12263
    s
    Participant

    Try to analyize the power quality and measure the THD ( total harmonic distortion) 

    s
    Participant

    What about power factors of those loads?

    it's vital to know them, P= 1.73 x V x I x cos(phy)

    in reply to: Convert single phase to three phase #12261
    s
    Participant

    If this cooker electricly is just an electrical heater you can try converting the cooker itself into 1 phase

    It has three windings, seperate the connections between windings, and energize every winding seperately,

    in reply to: elias #12260
    s
    Participant

    What do you mean by calculating time?

    in reply to: electricity charge for charging 2v 3000Ah batteries #12259
    s
    Participant

    You can think about it like this

    the coltage is 2 v

    3000Ah means that if the current is 3000A the battery will provide electrical energy for 1 hour

    so simply the formula is like this : E= 2 x 3000 = 6000 WH = 6 KWH energy required

     

    P.S : this calculations are for IDEAL enviroment, but could be applied 99% of times,

    in reply to: Total Resistance-Rt #12258
    s
    Participant

    1/Rt=1/R1+1/R2+1/R3+………………….+1/Rn

    Rt = Total resistance

    n = number of parallel circuits

     

    Also the same formula can be used for Z 

    in reply to: transformer rating #12256
    s
    Participant

    NO CAN DO, since P load > S transformer, end of story

    in reply to: how to find apparent power and reactive power? #12247
    s
    Participant

    Hi

    One mistake at my post

    P is the real power in Watt , S is the apperant power in VA

    S=Square root (Psqr + Q sqr)

    Just replace the word “REAL” instead of “apperant” in my previous post