labren sondhi

Forum Replies Created

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • in reply to: KW Calculation #11589
    labren sondhi
    Participant

    Sorry, the drop is not I x Z as indicated, but should be 

    I²xZ
    in reply to: KW Calculation #11587
    labren sondhi
    Participant

    Calculate your current from

     kW=√3VIcosф

    Work out your impedance Z from point A to B where A is at the sending end and B is 35 m away. Your voltage drop will be approximately I x Z. Your  voltage will drop by this amount.

    in reply to: PUMP POWER CALCULATION #11585
    labren sondhi
    Participant

    Ahamed,

    To complete the equation for pump power calculation: the pump power (kW)  will be equal to flow rate in cubic metres per second x density of fluid in kg/cubic meter x acceleration due to gravitational force, 9.81 m/second squared, x head in metres. The shaft power (kW) will then be this pump power/pump efficiency.

     

    in reply to: PUMP POWER CALCULATION #11575
    labren sondhi
    Participant

    AHAMED said:

    Dear Engineers,

     

    I need some details about to  how to calculate the pump power from the general mechanical details.


     
    The pump will be required to pump Qn cubic metres of water per second to a head of H metres at n efficiency. Work out the pump power from these parameters considering that water density is unity. Is this information usefull? Check the units on both sides of the equation. 

    Labren

Viewing 4 posts - 1 through 4 (of 4 total)