  • in reply to: cable size & material vs current capacity #12074
    erickench
    Participant

    What do you mean by purity of the material?

    erickench
    Participant

    0.99 PF is a very good number.

    in reply to: three phase power consuption calculations #12072
    erickench
    Participant

    One horsepower = 746 watts. For your problem the total HP = 746000 Watts. You can assume that this amount is consumed in one hour.

    in reply to: Thermal O/L Relay setting #12071
    erickench
    Participant

    NEC 430.32 gives the rules for sizing motor overloads. You must either determine the service factor which should be on the nameplate or determine the marked temperature rise also on the nameplate.

     

    Motors with a marked service factor 1.15 or greater                                           125%

    Motors with a marked temperature rise 40'C or less                                            125%

    All other motors                                                                                                  115%

    in reply to: cable size & material vs current capacity #12059
    erickench
    Participant

    Have you ever heard of this formula:

    Resistance = K x L/A

     

    The length L is in feet and the area A is in circular mils. K has two different values for copper and aluminum.

    Copper K = 12.9

    Aluminum K = 21.2

    in reply to: short circuits on panel boards . how to prevent? #12011
    erickench
    Participant

    A short circuit occurs because an ungrounded conductor comes in contact with ground or neutal conductor or another ungrounded conductor such as a double line-to-ground fault. NEC 408.36 has rules for the protection of panelboards. They state:

    a panelboard shall be protected by an overcurrent device having a rating not greater than that of the panelboard

     

    If there is a fire or some other accident occurs then the panelboard is not protected properly. The main circuit breaker is supposed to trip whenever a short circuit or overload occurs. Perhaps the available short circuit current exceeds that of the AIC rating?

    in reply to: parrallel operation of power transformer #12010
    erickench
    Participant

    erickench said:

    Transformers wil operate satisfactorily provided they have:

    1) the same ratio of transformation

    2) the same voltage ratings

    3) approximately the same regulation


    Distribution tarnsformers are used at the customer interface i.e. spot networks.

    in reply to: parrallel operation of power transformer #12009
    erickench
    Participant

    Transformers wil operate satisfactorily provided they have:

    1) the same ratio of transformation

    2) the same voltage ratings

    3) approximately the same regulation

    in reply to: load calculation #11976
    erickench
    Participant

    18.4 amps can't be correct. You must always assume that the AC and the heater are not going to operate at the same time. You must take the higher of these two loads in your calculations.

    in reply to: what is % impedance of transformer? #11972
    erickench
    Participant

    Typical transformer impedances are around %6. Have you tried performing a short circuit test?

    in reply to: 3 phase operating voltage #11971
    erickench
    Participant

    Are you sure it's three phase? It might be a single phase three wire 110/220 volt system. Picture a 220 volt transformer with a %50 center tap.

    in reply to: load calculation #11970
    erickench
    Participant

    What is the area in square feet? Is it just one apartment or the entire building?

    erickench
    Participant

    I would suggest using the KVA method in performing a short circuit calculation. You wouldn't have to use per units or complex numbers.

    in reply to: load calculation #11968
    erickench
    Participant

    Is it for a single apartment or foran entire multifamily building? NEC 220 has the procedures for calculating the load. What is the area in square feet?

    in reply to: Help me please… #11769
    erickench
    Participant

    It could very well be that power is being tapped upstream from the five submeters as you so call them and it's being used for something else. For instance hall and stairway lighting would not be charged to the tenants.