  • in reply to: Power System Operation and Control #13100
    Steven Mill
    Participant

    @guest said:

    very interesting article…bt tell me abt fuzzy logic and   lfc

     

    Thanks. I’ll write an article about LFC, you could read it at the beginning of next week.

    in reply to: Power System Operation and Control #12995
    Steven Mill
    Participant

    Hello, you’re welcome!

     

    Jeff Williams, sure next week I’ll post an article about AGC first.

    in reply to: Stability Factor: K-Factor #13000
    Steven Mill
    Participant

    Thank you for your feedbacks!

     

    Spir Georges GHALI, sorry for the late reply and thank you for your interesting remarks.

    @Spir Georges GHALI said:
    Dear;

    It’s very good and important to mention the effects of Harmonics on the Transformers, but I have some remarks that are :

    – I think the percentages of Harmonics currents mentioned in this topic mean the percentage of the “ THD-I ” ( Total Harmonic Distortion of Current ). If not, please clarify.

    Yes these percentages are of THD. Sorry If that confused you.

    – It’s known that the effect of K-Factor is to over-size the Transformer’s power, but what is the formula between the K-Factor and the Transformer’s power ?

    Normally in order to calculate the K-Factor you keep into account two things the KVA & load Harmonic Current. So accordingly the K-Factor would be:

     

    K – Factor = KVA * IL
     

    As IL is the load harmonic content so you can easily calculate the K-Factor value to be used.

    – You mention that “ the inductive loads like Motors are known as harmonic generating loads ”, but most of motors especially “ Squirrel Cage Motors ”, and after the transient running case are always “ Linear Loads ”, but for these loads the Harmonic currents can be generated or not depending on the kind of running equipment used to run these motors. ( for exp. Contactors with Thermal relays doesn’t generate any harmonic, VFD equipment generates harmonics ).

    I was specifically referring to induction motors which are widely used in industry as compared to squirrel cage motors which are most suited for small tasks. Very rare have I seen squirrel cage motors used in industry. Induction motors generate harmonics and come in the domain of non-linear loads. Also in industries the Switch mode power supplies & DC rectifiers also add to the non-linearity of the system.

    – It’s mentioned that “ the working principal of K-rated Transformers involves the use of a double sized neutral conductor ”, but in general, depending on the Harmonics Currents value or percentage, we over-size “ double or even more ” the cables’ sections of Phases & Neutral “, and also depending on the value or percentage of the “ Third multiple Harmonics ” and the “ Unbalance current’s value ” we decide the final section of neutral conductor.

    Yes you are right about conductor size. It depends on the harmonic currents value. I also wrote in the article that Some K-rated transformers use more than one conductor. Normally you don’t need a transformer with K-factor rating more than K-4 or K-13 in industries which are coherent to the design specs presented in the article.

    – As mentioned, the K-Factor Value’s range is from “ 1 ” to “ 50 ”, and also, the rules mentioned the K-Factor Transformers that should be used depending on the Harmonic Current, ( exp. for Harmonics Currents more than 75% the “ K-20 Transformers ” should be used ) but, at which levels or where the values “ K-30  or  K-35 Transformers ” or more should be used ?

    Transformer size increase as you increases the value of K-Factor & so does the heat tolerance due to harmonic currents. Normally transformers of K-Factor 30, 40 & 50 are used where harmonic currents are somewhere b/w 125-150%. These are worst harmonic conditions. As mentioned before the size of transformer increases with the increase in K-Factor so the optimal K-Factor should be chosen which would be a tradeoff between transformer size & its heat tolerance. Normally the K-50 transformers are very expensive & much larger in size so manufacturers recommend a transformer of K-30 with modified designs as a replacement.