  • in reply to: High Voltage: circuit breaker is cheaper! #12538
    IHOORA MICHAEL
    Participant

    I agree with you sir, for me am a substation attendant and every thing is possible with use of circuit breakers, regarding resetting in case of a trip and faults are easy to identify with the use of CBs. Imagine of a fuse blowing and you want to replace it, you will take alot of time de-assembling and assembling the components in order to replace the fuse.

    in reply to: Lightning Protection #12329
    IHOORA MICHAEL
    Participant

    My regards;

       The number of down
    conductors can be determined as follows:

    1-One conductor for a structure whose base area does not
    exceed100 sq m

     

    2-Determine the whole numbers N1 and N2, and select the
    smaller of the two

           
    N1=1+(A-100)/300

     

            N2=P/30

     

      Where N=whole number
    of the working area

                  A=base
    area of the structure in sq m

                 
    P=perimeter of the structure in m

     

    3-Where the height of the structure is more than 30m in
    height, additional considerations             to
    the above should be applied.