  • in reply to: what is % impedance of transformer? #11962
    freak16
    Participant

    The normal method
    of  expressing  transformer  impedance  is  as  a  percentage  voltage  drop  in  the
    transformer at full-load current and this reflects the way in which it is seen by
    system designers. For example, an impedance of 10% means that the voltage
    drop at full-load current is 10% of the open-circuit voltage, or, alternatively,
    neglecting any other impedance in the system, at 10 times full-load current, the
    voltage drop in the transformer is equal to the total system voltage.

    Formula written by MH is perfect.

    Thenormalmethod
    ofexpressingtransformerimpedanceisasapercentagevoltagedropinthe
    transformeratfull-loadcurrentandthisreflectsthewayinwhichitisseenby
    systemdesigners.Forexample,animpedanceof10%meansthatthevoltage
    dropatfull-loadcurrentis10%oftheopen-circuitvoltage,or,alternatively,
    neglectinganyotherimpedanceinthesystem,at10timesfull-loadcurrent,the
    voltagedropinthetransformerisequaltothetotalsystemvoltage.Expressed
    insymbolsthisis:
    Vz %Z
    IFLZ
    E
    100
Viewing 1 post (of 1 total)