elec master
Participanti think this will depend if the electrical sources in your network will be considered as separately drived systems or not , for separately drived system , we must use 4 pole circuit breaker to disconnect the neutral of the two sources ( transformer and generators or 2 generators ) to prevent earth fault in the main switchgear.
you can digg the NEC code for the expression ” separately drived systems” and you will find the answer or got to the following site which explain the NEC code by following the link:
Understanding NFPA 70 (National electrical code) course
elec master
Participantthis done by adding power factor correction capacitors (PFCC) , you must know the following data:
1- the load (kw) that you need to improve its power facto
2- the old power factor value
3- the new power factor value
then you can use the power factor correction tables to calculate the required capacitor KVAR or using the PFCC calculation spread sheet which you can find it in this link:
after you know the required KVAR, you must select the the capacitor sizes ,numbers and steps but you must defierntiate between electrical steps and the phisycal steps which i will explain it in a new reply.sorry , i must leave now.