  • in reply to: Best electrical calculation software review #12343
    Ally Kanyondo
    Participant

    Dear All,

    The mentioned software are Good but the best one is SOLUTIONS ELECTRICAL SOFTWARE. Currently im using this software.

    IT is capable of doing the following:-

    CABLE CALCULATIONS

    CIERCUIT DESIGNER

    INSTALLATION SIMULATOR

    AIR CONDITIONING SIZES

    HEATING CALCULATIONS

    HEATING ELEMENTS

    SHORT CIRCUIT CALCULATIONS

    TEST INSPECTION FORMS

    ISTALLATION OPTIMIZER

    ELECTRICAL ESTIMATOR

    PROTECTION AND COORDINATION

    BOARD TEMPERATURE

    POWER FACTOR CORRECTION

    TRANSFORMER REGULATION

    MAX DEMAND FOR DOMESTIC

    MAX DEMAND FOR INDUSTRIAL.

     

    I advise you to try on this software.

    For more informations you can visit the following web: http://www.solutionselectricalsoftware.com

     

    Kind regards

    in reply to: sizing load ,cable& breaker #12342
    Ally Kanyondo
    Participant

    Dear Mr Ghali

     

    Thanks very much for your clarifications. I am also begging you to pass through my article in the general discussion entitled

    “LIGHTNING PROTECTION” or

    Tell me or send me softcopy of any good electrical books about protection.

    My email address is: allygk@gmail.com

     

    Be much blessed for helping us young and emerging engineers.

     

    Kind regards

    in reply to: sizing load ,cable& breaker #12339
    Ally Kanyondo
    Participant

    Spir Georges GHALI said:

    ally said:

    Dear Ghali

     

    Let me add to the above question,

     

    Assume the ratings are as follows:-

    1. Transformer rating is 1000kVA, 11kV/0.4kv

    2. Type of earthing system is TN-C

    3. Cable length is 35m.

     

    Help us to calculte the remaining items(short circuits).

     

    I real appreciate your solutions.

     

    Your are a real MENTOR most of in the forum.

     

    Regards.


    Dear Mr. Ghali ;

    I was reading your solution but i am little confused on how you get those data highligted in red colour. Please let me know

    where did you get those data below.

    Kind regards

     

     

    – Medium Voltage :

    We have the following information :

    – The value of the Short Circuit Power on ” 11 kV ” is : ” Scs ≈ 500 MVA “

    – The Voltages : 11 / 0.4 kV

    RMV / ZMV = 0.1

    So :

     ZMV = U2 / Scs   →   ( 1.05 x 400 )2 / 500 x 106   →   ZMV = 0.352 mΩ

    Rem. : as we should calculate the values of ” R  &  X ” from LV side of transformer, we can use directly ” 400V “, or we use ” 11kV ” but in this case and after calculation we should multiply the result by the ” SQR of the Transformer Ratio – ( 11/0.4 )2  “.

    RMV = 0.1 x ZMV    →                                                                      RMV = 0.035 mΩ

    XMV2 = ( ZMV )2 – ( RMV )2    →    ( 0.352 )2 – ( 0.035 )2    →         XMV = 0.35 mΩ 

     

    – Transformer :

    As the Transformer's power is ” Sn = 1000 kVA   →   In = 1445 A ” and I haven't the other information, I will assume that :

    – Usc = 6 % ( percentage of Short Circuit Voltage )

    – Wtr = 15 kW ( full load Copper Loses )

    So :

    ZTR = Usc x U2 / Sn   →   0.06 x ( 400 )2 / 1000 x 103   →               ZTR = 9.6 mΩ

    RTR = Wtr / 3 x In2   →   15000 / 3 x ( 1445 )2   →                          RTR = 2.39 mΩ

    XTR2 = ( ZTR )2 – ( RTR )2    →   ( 9.6 )2 – ( 2.39 )2    →                XTR = 9.29 mΩ

    Rem. : if the values of ” Usc  &  Wtr ” are different, the calculation should be re-done.

     

    – Cables :

    As the previous cables have been defined accordingly to the Loads' Current ” 1175 A “, but now :

    – They should be defined accordingly to the transformer's nominal current ” 1445 A “

    – The number of cables per phase will be more than 4

    – These cables will be installed on 2 Cable Trays.

    So, The Reduction Factors are :  0.81   &   0.61

    By doing the same previous calculation, we obtain the cables' sections in the same working conditions that are :

    – For each Phase        : ” 5 Single Core Cables of  300 mm2

    Regarding the following points :

    – All loads are ” 3 Phases “.

    – Assuming that we haven't the 3rd harmonic.

    – The used Earthing System is ” TN-C “.

    We can use the following cables :

    – For  PEN                   : ” 1 Single Core Cables of  300 mm2

    Calculation of ” X ” for Cables :

    As the Installation's Method is ” Touching – Flat “, the ” X  per 1m = 0.13 mΩ/m “, so :

    Xca( Ph ) = 0.13 x 35 / 5    →                                                                Xca( Ph ) = 0.91 mΩ

    Xca( PEN ) = 0.13 x 35    →                                                                   Xca( PEN ) = 4.55 mΩ

    Calculation of ” R ” for Cables :

    As the Resistivity ” ρ “of Copper is different between the ” Cold ( 20 °C )  or  Hot ( 70 °C ) ” states of cables, we should calculate ” R ” in these 2 states, that we do as follow :

    In Cold state ” 20 °C ” :

    Rca(20)( Ph ) = ρ x L / S = 18.51 x 35 / 5 x 300    →                              Rca(20)( Ph ) = 0.432 mΩ

    Rca(20)( PEN ) = ρ x L / S = 18.51 x 35 / 300    →                                 Rca(20)( PEN ) = 2.159 mΩ

    In Hot state ” 70 °C ” :

    Rca(70)( Ph ) = 1.23 x ρ x L / S = 1.23 x 18.51 x 35 / 5 x 300    →          Rca(70)( Ph ) = 0.531 mΩ

    Rca(70)( PEN ) = 1.23 x ρ x L / S = 1.23 x 18.51 x 35 / 300    →             Rca(70)( PEN ) = 2.656 mΩ

     

    Calculation of Short Circuit Currents :

    To calculate the ” Loop Impedances ” of Short Circuits, it will be better to integrate all results in a table like the following :

     

    Component

    X : mΩ

    R : mΩ

    1

    Medium Voltage :

    500MVA – 11/0.4kV

    0.35

    0.035

    2

    Transformer :

    1000kVA – 6% – 15kW

    9.29

    2.39

    3

    Cables :

     

    20 °C

    70 °C

    Phase : 5 x 300mm2

    0.91

    0.432

    0.531

    PEN    : 1 x 300mm2

    4.55

    2.159

    2.656

     

    Calculation of the maximum Short Circuit Current ” Isc3max ” :

    We assume in this case that we have a short circuit between ” 3 Phases ” at the input of MDB but the cable are in the ” Cold ” state :

    Isc3max = Cmax x Uo / 1.73 x Zsc      ,      where :

    – Cmax = 1.05

    – Uo = 400V

    Zsc2 = ( 0.35 + 9.29 + 0.91 )2 + ( 0.035 + 2.39 + 0.432 )2     →                         Zsc = 10.93 mΩ

    So :

    Isc3max = 1.05 x 400 / 1.73 x 10.93 10-3      →   Isc3max = 22.21 x 103 A      →    22.21 kA

    The Breaking Capacity of the Circuit Breaker should be  ” BC  ≥  23 kA “

    Rem. : The ” Isc3max ” at the Transformer's Output is ” 24.42 kA “.

     

    Calculation of the minimum Short Circuit Currents ” Isc1min   &  If ” :

    As we have ” PEN ” that means the ” Isc1min  &  If ” have the same value, so, we will calculate only one.

    We assume in this case that we have a short circuit between ” 1 Phase & PEN ” at the input of MDB but the cable are in the ” Hot ” state :

    Isc1min = If = Cmin x Vo / Zsc      ,      where :

    – Cmin = 0.95

    – Vo = 231 V

    Zsc2 = ( 0.35 + 9.29 + 0.91 + 4.55 )2 + ( 0.035 + 2.39 + 0.531 + 2.656 )2   →     Zsc = 16.109 mΩ

    So :

    Isc1min = If = 0.95 x 231 / 16.109 x 10-3     →   Isc1min = If = 13.62 x 103 A      →   13620 A

    The Magnetic Protection should be adjusted at ” Im = 10600 A “ or smaller accordingly to the protection unit adjustments.

     


    in reply to: sizing load ,cable& breaker #12337
    Ally Kanyondo
    Participant

    Dear Mr Ghali.

     

    Thanks for the additoinal informations.

    i am also Concerned about the Lightining protection.

    I want  to know how i can calculate the maximum covereage of lighting arrestors in high rise buildings and in those builidings in which the

    lightning protection device is provided at the highest point of the building like church towers.(as there is a maximum area any lightning

    protection device can cover).

     

    Thanks again in advance.

    Hope to hearing from you soon.

     

    Best Regards.

    in reply to: sizing load ,cable& breaker #12331
    Ally Kanyondo
    Participant

    Dear Mr. Ghali

     

    Thank you very much for your solution. Now i can calculate the short circuits at different levels

     

    by using your knowledge as you gave us above.

     

    Be blessed and hope to get and leran a lot from you.

     

    Kind Regards.

    in reply to: sizing load ,cable& breaker #12321
    Ally Kanyondo
    Participant

    Dear Ghali

     

    Let me add to the above question,

     

    Assume the ratings are as follows:-

    1. Transformer rating is 1000kVA, 11kV/0.4kv

    2. Type of earthing system is TN-C

    3. Cable length is 35m.

     

    Help us to calculte the remaining items(short circuits).

     

    I real appreciate your solutions.

     

    Your are a real MENTOR most of in the forum.

     

    Regards.

    Ally Kanyondo
    Participant

    Dear Ghali,

    Thank you very much for briefly explanation.

    You have provided me the way forward.

    I thought there will be a formula for that but it seems only the utillity company can set the levels.

     

    Kind Regards.

    in reply to: Load-Shedding survey and discussions #12305
    Ally Kanyondo
    Participant

    Dear Laurent

    I have been trying to access it several times but im told im already registered. What can i do now 


    in reply to: electrical design engineering books/info #11629
    Ally Kanyondo
    Participant

    HI Jenny just go to 4shared website and type this”tansmission and distribution” then search in the link titled books.

    you will get the exactly book. i just did that n got it.