Re: Faults

#12912
olivier bouilliez
Participant

Could you please add details to your question ?

I presume that you are speaking of LV panels .

If the breaker trips, and there is no other switching device downstream, then anyway the load is unpowered . So the best way is first visual inspection and then disconnect the circuit as downstream as possible and measure the circuit impedance . If OK, repeat upstream until you locate the S C area .