    How  to identify short circuit take place at the end of outgoing power of circuit breaker in a panel when load is connected.

    #12912
    olivier bouilliez
    Participant

    Could you please add details to your question ?

    I presume that you are speaking of LV panels .

    If the breaker trips, and there is no other switching device downstream, then anyway the load is unpowered . So the best way is first visual inspection and then disconnect the circuit as downstream as possible and measure the circuit impedance . If OK, repeat upstream until you locate the S C area .