Re: Air condition load

#12309
Spir Georges GHALI
Participant

Freeknow said:

Hi  dears

I have 70 Unit of A/C unit 3phase 220 Current rated as in name plate is 23.5. My Qusi  I want to total load for these units and feeder size, condsider ambeint tempreture is 55 degree.

With best   


Dear ;

 

Please confirm the following points to be able to do the calculation :

– Supply : 3 Phases – 220V : is this value between 2 phases ?

– The rated current for each unit is : 23.5 A

– The Power Fcator ” Cos φ ” for unit ?

– Haw many units will be in working in the same time ? ( to define the Utilisation Factor – Ku )

– What kind of cables you use normally ” PVC  or  XLPE ” ?  Cu  or  Alu ?

– What Methode of installation you will use ” Unperforated  or  Perforated cable tray, Ladder, … ” ?

– Are you sure that the ambiant temperature inside where the cables will be installed is ” 55 °C ” ?