Air condition load

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #10544
    Freeknow
    Participant

    Hi  dears

    I have 70 Unit of A/C unit 3phase 220 Current rated as in name plate is 23.5. My Qusi  I want to total load for these units and feeder size, condsider ambeint tempreture is 55 degree.

    With best   

    #12309
    Spir Georges GHALI
    Participant

    Freeknow said:

    Hi  dears

    I have 70 Unit of A/C unit 3phase 220 Current rated as in name plate is 23.5. My Qusi  I want to total load for these units and feeder size, condsider ambeint tempreture is 55 degree.

    With best   


    Dear ;

     

    Please confirm the following points to be able to do the calculation :

    – Supply : 3 Phases – 220V : is this value between 2 phases ?

    – The rated current for each unit is : 23.5 A

    – The Power Fcator ” Cos φ ” for unit ?

    – Haw many units will be in working in the same time ? ( to define the Utilisation Factor – Ku )

    – What kind of cables you use normally ” PVC  or  XLPE ” ?  Cu  or  Alu ?

    – What Methode of installation you will use ” Unperforated  or  Perforated cable tray, Ladder, … ” ?

    – Are you sure that the ambiant temperature inside where the cables will be installed is ” 55 °C ” ?

    #12312
    Spir Georges GHALI
    Participant

    Dear ;

     

    As we have on the name plate the rated current, so, we don't need Cos φ.

    #12317
    Spir Georges GHALI
    Participant

    Dear ;

     

    As there's no answer till now, please find bellow the calculation of the Cables' Sections.

    Assume that :

    • ” Ku ≈ 70 % ” that means  50  of  70 AC  are working in tha same time.
    • The Methods of Installation :

                   – ” Horizontaly Perforated Cable Tray “

                   – ” Touching – Flat “

    • ” Only 1 Cable Tray “
    • The kind of Cable : ” Single Core Cable – Copper – PVC “

    The total load current :  Ib = 50 x 23.5 = 1175 A

    The Reduction Factors will be defined accordingly to the following points :

    • 3  or  4  cables per Phase  →  The Reduction Factor : 0.87
    • The Ambiant Temperature is ” 55 °C ” in the air  →  The Reduction Factor : 0.61

    So, the total Reduction Factors is : 0.87 x 0.61 = 0.5307

    And the nominal current for needed cables is : 1175 / 0.5307 = 2214 A

     

    Suppose that we will use ” Single Core Cable – 300 mm2 “, and from table ” A.52-10 ” of ” IEC 364-5-52 “, we find that the Current Carrying Capcity for ” 300mm2 ” for ” Touching – Flat / Methode F ” is ” 587 A “, the number of cable per phase is : 2214 / 587 = 3.77 

    So, we will use :

    • For each Phase        : ” 4 Single Core Cables of 300 mm2
    • For Neutral              : ” 2 Single Core Cables of 300 mm2

    Noting that :

    • For Neutral : as all loads are ” 3 phases “, and we haven't the 3rd Harmonic.
    • If ” Ku ” is different, the calculation should be re-done.

     

    After that, you should calculate the ” Drop Voltage “ to know if these cables are suitable or not.

     

    Regards.