Home › Electrical Engineering Forum › General Discussion › Zig Zag Transformer
- This topic has 2 replies, 3 voices, and was last updated 15 years, 3 months ago by
erickench.
- AuthorPosts
- 2010/12/22 at 7:15 pm #10321
abrahan
ParticipantDelta winding grounding with Zig Zag Transformer.
what is Zig Zag Transformer??
what is the advantages??
how it will connect with delta windingof the main transformer.
2011/01/03 at 1:33 pm #11716Nawaz
ParticipantIn delta zig-zag connection the primary is connected in delta.Each secondary winding is made in two halves such as a1-a2,b1-b2,c1-c2 and the six halves are then connected to form a zig zag connection.A1,a1,a2 are of same polarity and similarly for other phases.If the voltage of each half of the transformer secondary is V1/2,the pjase voltage of the secondary system is (sqrt(3)/2)*V2 and the line voltage is 3/2*V2. Thus in delta zig zag connection the line voltage transformation ration is 1.5 times the phase turn-ratio is 3/2 times line transformation ratio.
A zig-zag transformer is a special form of autotransformer used to provide grounding (earthing) on three-phase systems that otherwise have no connection to ground . It has primary windings but no secondary winding.They provides a path for current that is common to all three phases.Another application includes control of harmonic currents
2011/01/07 at 3:19 pm #11722erickench
ParticipantI would say that a zig-zag transformer is used to derive a neutral from a delta sytem.
- AuthorPosts
- You must be logged in to reply to this topic.