Why Is Isolated Neutral Preferred In Some Turbines/Generators?

Home Electrical Engineering Forum General Discussion Why Is Isolated Neutral Preferred In Some Turbines/Generators?

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #10599
    GT
    Participant
    Dear engineers,

    I need your help in analyzing this query:

    Our plant consists of 11x 635 KW, 415V Waukesha gensets, 2 x
    3.5MW,11KV wartsila gensets, 11 KV main bus for synchronization & 10
    MW,11KV, 50 Hz gas turbine. The neutral of gas turbine is earthed
    against the manufacturers recommendations.

    Now, a 2.7MV, 11KV, 50 Hz steam Turbine is being added to the system whose neutral is recommended to be earthed. but before taking this action the Neutral of existing Gas Turbine is to be un-earthed.

    So, Under which conditions the Neutral of a generator should be earthed & what are the conditions when “isolated neutral” is recommended?

     

    I am not asking from manufacturer's point of view but I am simply asking
    from synchronization point of view. Any questions will be welcomed!

    THANKING IN ADVANCE :)

    #12415
    admin
    Keymaster

    You can only have one neutral solidly earthed at each foltage level, w/o causing spurious tripping problems for sensitive earth fault relais systems.

Viewing 2 posts - 1 through 2 (of 2 total)