- 2013/05/14 at 2:23 pm #11004
yudhi
ParticipantHi I am yudhi
I have problem with voltage drop ,
When the load at 3400 amp the voltage drop until 360 volt
I use 4000 kva step down transformer from 20 kv to 400 volt.
The cable is NYY 1x400mm , 8 cable for each phase at 400 volt
And 1x120mm at 20 kv, cos q is 0.9
Distance grom transformer to switchboard around 60 mtrI dont know where the problem
I hope you guys can help me to solve this problemRegards
Yudhi2013/06/06 at 8:55 am #13121admin
KeymasterHi yudhi,
Your posted has been moved to the right section of the forum, “General discussion”. Now the community will see your topic and probably help you.
2013/06/06 at 9:49 am #13078Spir Georges GHALI
Participant@yudhi said:
Hi I am yudhiI have problem with voltage drop ,
When the load at 3400 amp the voltage drop until 360 volt
I use 4000 kva step down transformer from 20 kv to 400 volt.
The cable is NYY 1x400mm , 8 cable for each phase at 400 volt
And 1x120mm at 20 kv, cos q is 0.9
Distance grom transformer to switchboard around 60 mtrI dont know where the problem
I hope you guys can help me to solve this problemRegards
YudhiDear ;
First, by calculating the voltage drop of cables between the transformer and switchboard, I found that should be around “ 1% ”, noting that I assumed the arrangement of these cables is “ Trefoil ”, but let me know if the mentioned voltage drop “ ≈5% ” is only for this distance ? Or in a another place of network ?
If it’s only of this distance, you should do the following :
– Measure the output voltage of the secondary’s transformer at no-load.
– if it’s “ 400V ”, we should know the specifications of the transformer and the length of MV line to be able to calculate if this phenomena is caused by MV line.
– if the output voltage is smaller than “ 400V ”, the reasons are either the MV voltage is less “ 20kV ” (you should know this value), or the position of the “ Tap-off changer ” is not correct, in all cases, try to change this position to have around “ 400V ” or even just a little more.
– if this voltage drop is in another place of network, please let me the type, section, length, and arrangement ( if it’s Single Core ) of that cables to be able to calculate the voltage drop at that point.