two phase power calculation

Home › Electrical Engineering Forum › General Discussion › two phase power calculation

Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #10505
    jatin333
    Participant

    if there is three phase power system we calculate power kw= sqrt(3)*V*I*CosØ so what is formula for two phase system?

    #12163
    Spir Georges GHALI
    Participant

    jatin333 said:

    if there is three phase power system we calculate power kw= sqrt(3)*V*I*CosØ so what is formula for two phase system?


    Dear Mr. Jatin333

     

    To calculate the power value accordingly to : Voltage, Current, and Power Fcator, we have the following formula :

    – For 3 Phases plus or withour neutral :

              P = sqrt(3) x U x I x Cos Ø

    – For 2 Phases :

              P = U x I x Cos Ø

    – For 1 Phase + Neutral :

              P = V x I X Cos Ø

     

    where :

    U : Voltage between 2 pahses in ” Volt “

    I : Current line in ” Amp “

    V : Voltage between phase & neutral in ” Volt “

     

    Regards.

    #12169
    jatin333
    Participant

    thanx Mr.

    Spir Georges GHALI

Viewing 3 posts - 1 through 3 (of 3 total)
  • You must be logged in to reply to this topic.