2011/05/28 at 2:43 pm #10495adminKeymaster
Is there any value per standard to use as reference for Total Harmonic in the system. What is the value we can say it is safe for a sensitive instrument.
Need to educate me, how the hamonic and distortion is appearing in the electrical system?please need your expert advice, thanks
2011/06/01 at 9:26 am #12121Spir Georges GHALIParticipantpaule said:
Is there any value per standard to use as reference for Total Harmonic in the system. What is the value we can say it is safe for a sensitive instrument.
Need to educate me, how the hamonic and distortion is appearing in the electrical system?please need your expert advice, thanks
Dear Paule ;
First, the harmonics currents are generating by the Elctronics Loads like : Computers, Printers, Faxes machines, Variable Speed Drives, DC Drives, Electrnic transformers for lighting, ext. These loads generates the Harmonics Currents, and all distortion of currents we called ” THD I – Total Harmonic Distortion of Current ” that affacte the voltage sine wave ( becuase we have the Harmonic Impedances ), so, we have that we called the distortion of Voltage ” THD U or THD V “. Noting that the most importatnt value is ” THD U or THD V “.
The ” IEC 61000-2-2,3,… ” defines the maximim percantages value of Voltage Distrotion of each harmonic for ” HV, MV, and LV networks, for exp. for LV networks : for n=3, the maximum is ” 5 % “, for ” n=5 ” the max is ” 6 % “, and also this IEC… defines these percantages for Odd & Even Harmonics. In France, the EDF defines the max percantage of ” THD V ” on the LV networks by ” 5 % “.
Regards.
2011/06/04 at 7:27 am #12136adminKeymasterThanks, if its exceeds the maximum value of 5 % for n=3 and 6 % for n=5, what will be the impact in the connected instrument or devices, does it will damage the instrument?what precaution or protection we can apply.
2011/06/05 at 9:40 am #12143adminKeymasterHi
You can download “IEEE-519-1992” standard about THD, it's a good referenace.
2011/06/09 at 10:20 am #12165Spir Georges GHALIParticipantpaule said:
Thanks, if its exceeds the maximum value of 5 % for n=3 and 6 % for n=5, what will be the impact in the connected instrument or devices, does it will damage the instrument?what precaution or protection we can apply.
Dear Mr. Paule ;
If the Voltage Harmonic Distortion for each harmonics exceeds the value defined by standard, that means the Total Harmonic Distortion of Voltage ” THD U or THD V ” will be globaly more than standardrized valeus, that can creats some disturbances in working of instruments, and even the currents for lieanr Loads will be distorted.
By the way, when we have these high percentages of THD U, that means we have big percentages of current distortion ” THD I “, that leads to increase the losses in transformers, generators, cables, and also the heating of these equipments will be more. In some cases when we have a big value of ” THD I ” but the ” THD U ” is less than the stadard value, we should in this case dereat the power of Transformes and Generators, and also over-size the section of cables.
In the same time, the most dengarous harmonics are the Double Third Harmonics, that means : 3, 9, 15, …, because these harmonics have the same vector,so, the sum of them aren't ” 0 ” and they run in the neutral cables, for this reason once we have this kind of harmonics in the network, we should calculate the value of them and do correctly the choice of the neutral cable's section. But most of the maufacters of some elctronic equipments like : Virable Speed Drives, UPS, try to minimize the percentages of them in their euipments. Noting that in some equipments of serious manufacters the percentages of this kind of harmonics are ” 0 “.
Regards.
-