    Hello, everybody.

    I've got many single-phase loads, which make about 10 kVA together. Assuming that the UPS input is three-phase, I wonder which is the better choice for the output: single-phase or three-phase?

    Thanks in advance for your help

    #11894
    admin
    Keymaster

    I will encourage you to use a three phase, it is much better.

    #11895
    admin
    Keymaster

    but 3 phase is so complicated………..

    #11897
    simone
    Participant

    What do you think are the pros and cons of each option?

    I would really appreciate a technical discussion about this issue.

     

    Thanks

    #11898
    Chris2011
    Participant

    I think 3 phase is better.

    #11899
    Alen Matanovic
    Participant

    Three phase will offer some harmonics cancelation of your nonlinear loads (I assume that there are mostly nonlinear loads, since you need UPS),, but you'll still have problems with “simetry” of your loads.. It actually really depends on type of your loads..

    #11901
    simone
    Participant

    Alen,

     

    You're right. Most of the loads are nonlinear: mainly PCs and some other electronic devices. I don't think there is any problem with “simetry” of the loads if there is a correct planification of the distribution among the three phases, before starting the installation. The fact is that I'm trying to find out if there is any strong argument which makes one option really better than the other one, but so far there isn't.