2011/06/30 at 9:42 am #10530nagarajuParticipant
Dear Engineers,
Greetings.
I want to be know about synchroniziation with full fledged details,regarding example of generators and transmission lines also
thanking you.
2011/07/07 at 9:54 am #12292Spir Georges GHALIParticipantnagaraju said:
Dear Engineers,
Greetings.
I want to be know about synchroniziation with full fledged details,regarding example of generators and transmission lines also
thanking you.
Dear ;
We use the Synchronization to be able to connect 2 sources on parallel to the same bus-bar, so, to do it we should realize the following conditions :
– The Value of ” Voltage ” for both should be exaclty the same.
– The Value of ” Frequency ” for both should be exactly the same.
– The direction of ” Rotation ” of pahses should be the same.
– There's no any ” Phase shift ” between them at the moment of connection.
– It will be better that :
– The powers are the same.
– The specifications are the same.
– The manufacture for both is the same ( to be sure that they have the same specifications ).
There's now special equipments that can do it automatically, or another can provide a signal once these conditions are realized, so, we can connect them manually but in this case it should be done immediately after the signal.
Assume that we want to connect 2 generators on parallel, where they have the same specifications mentioned above, in this case, at least one of them should have the possibility ” manual or Electrical ” to adjust : the Voltage and the Frequency ( by changing the r.p.m. of the engine ) that will be used to adjust these values to be the same as the 1st source. The procedure to connect them is as follow :
– We run the 1st generator, close the relative CB, so the Synchronization equipments will measure the ” Voltage & frequency ” for it.
– We run the 2nd generator, so, the Synchronization equipments will measure the ” Voltage & the frequency ” for it, and in the same time the ” Shift phase ” apparatus will measure the ” Shift angle ” between them.
– We adjust the ” Voltage ” value for the 2nd to be exactly as the 1st.
– We adjust the ” frequency ” value for the 2nd to be exactly as the 1st.
( these adjustments can be done also automatically by the Synchronization equipments if the 2nd generator is equipped ).
– If the connection will be done automatically, the Synchronization equipments will do it once the conditions are realized, but if will be done manually, we should monitor the ” Shift phase ” apparatus and once the value of the shift angle is ” 0 ” we close immediatly the CB for the 2nd generator.
If the powers of these 2 generatos aren't the same,in this case we should use also the ” Load Shearing Apparatus “.
-