    I have 2 generators each rated 5.6MVA, 6.3kV terminal voltage and 0.9pf  to be stepped up by 2 lots 6MVA power transformers. Should I use 1000A or 1250A CB immediately after each transformer for protection? Anyone with an answer please help.

    #13229
    vijay
    Participant

    1000A is ok