2014/01/01 at 2:03 pm #11119mohamed sleemParticipant
How about the size of the grounding conductor for the feeder 8 sets of (4x1c 630mm2)?
Applied for:
Cross-sectional area of phase conductors mm2 Minimum cross-sectional area of the corresponding protective conductor (PE, PEN) mm2 S < 16 S 16 < S < 35 16 35 < S < 400 S/2 400 < S < 800 200 800 < S S/4 2014/01/06 at 12:42 pm #13398mohamed sleemParticipantIf we are doing TN-C-S system and the cable protection is a breaker, would the 1x300m2 be acceptable with a feeder 8 sets of (4x1c 630mm2)? & if all of the sets installed in group the 8x1c300m2 will be ok?
Thank you,
2014/01/06 at 1:45 pm #13399Spir Georges GHALIParticipant@mohamed sleem said:
If we are doing TN-C-S system and the cable protection is a breaker, would the 1x300m2 be acceptable with a feeder 8 sets of (4x1c 630mm2)? & if all of the sets installed in group the 8x1c300m2 will be ok?Thank you,
Dear Mr. Mohamed ;
First at all, if you use ” TN-C-S ” as Earthing System , that means at the 1st level or maybe at the 2nd level also you have ” TN-C ” and ” PEN “, for that it will be better to do as follow :
– Check the Single-phase loads if they are distributed on 3 phases ( even if there’s some difference ).
– Check if the ” multiple third Harmonics ” are existed, if yes, you should know the percentage of each one.
Then, according to the results of these checkings, we can decide the section of ” PEN ” as follow :
– If the Single-phase loads are well distributed, and the percentages of the ” multiple third Harmonics ” are small and/or the total current of them is small, we can assume that ” 1x300m² ” or ” 2x240m² ” are enough, then we should calculate the Earth Fault Current for one of these 2 sections, and check if the chosen section can withstand the ” Thermal Stress ” of the Earth Fault Current during at least 1 or 2 sec ( certainly not more than 5 sec ), it not we should oversize the PEN’s section to ” 3x240m² ” or ” 2x300m² ” and repeat the procedure.
– If the percentages of the ” multiple third Harmonics ” aren’t small, it will be better to know the total current of them either by calculation or from the catalogues of the equipment generating these Harmonics, then we can use the same procedure that we use to define the Phases’ sections to define the section of ” PEN “, do the calculation of the Earth Fault Current, then check if the PEN cable can withstand the Thermal Stress.
By the way, and for ” TN-C ” system, please note that in all case the setting of the ” Magnetic or Short-time Protection ” should be smaller than the Earth Fault Current value by ” ≥ 20% “.
2014/01/06 at 3:00 pm #13400mohamed sleemParticipantDear Mr. Ghali,
First off, i should thank you for the elaborated reply, basically i’m responsible to do the building design & cannot get such deep information before the actual operation, of course during the design we can estimate the percentage of the harmonics at the feeder or circuit, so if you are in my place where making the design, what is the ideal steps when sizing the grounding conductor? most of the designers always sizing the grounding conductor to half of the phase which is completly uneconomical, at the same time we don’t want to loose the protection by anyway because of some extra cost.
-