    as it is said that we need to reduce the kvar to improve the power factor,but it is also said that we require kvar for the excitation of induction motor,so can you say that what is the main importance in power system network.

    #11790
    shivamshiva
    Participant

    Transformers and induction motors require kvar or consumes kvar where as
    capacitor banks will produces kvar. If there are no capacitor banks the
    generator will supplies kvar to the induction motors. Due to this power
    factor will reduces and current drawn from the generator will be more.
    If we install capacitor banks to supply the required kvar to induction
    motor then the kvar supplied from the generator will reduces and power
    factor will increases. Due to this current will reduces and losses will
    also reduces.