- 2011/07/08 at 12:11 pm #10538
mkomaravelly
ParticipantDear All,
I have a requirement for Transformer..
7.5hp Motor with 3 Phase, 415Volts, For this requirement I need a Transformer.
Can any body suggest me required 3 Phase Transformer Capacity for the above said requirement.
Thank you.
2011/07/09 at 8:37 am #12296Spir Georges GHALI
Participantmkomaravelly said:
Dear All,
I have a requirement for Transformer..
7.5hp Motor with 3 Phase, 415Volts, For this requirement I need a Transformer.
Can any body suggest me required 3 Phase Transformer Capacity for the above said requirement.
Thank you.
Dear ;
Fisrt, this motor is a small & standard motor, and you can run it by using any ” 3 Phases + Neutral / 415/239V “, so, why you need a transformer ?
Please, explain more about the kind of supply that you have.
2011/07/09 at 9:29 am #12297mkomaravelly
ParticipantDear,
We have got a requirement from customer side, more over its in Agricultural Area. Customer is preferring 3 Phase 10kVA Rating Transformer for the above mentioned hp.
Instead of 10kVA, we wanted to supply him 16kVA for other issues.
So,please reply me.
Thank You.
2011/07/09 at 11:49 am #12298Spir Georges GHALI
Participantmkomaravelly said:
Dear,
We have got a requirement from customer side, more over its in Agricultural Area. Customer is preferring 3 Phase 10kVA Rating Transformer for the above mentioned hp.
Instead of 10kVA, we wanted to supply him 16kVA for other issues.
So,please reply me.
Thank You.
Dear ;
Refer to your answer, please note that the procedure to define the Power of transformer is as follow :
– The motor's power in ” kW ” is : 7.5 ( HP ) x 0742 = 5.5 kW
– The needed power assuming that ” Cos φ = 0.85 ” = 5.5 / 0.85 ≈ 6.5 kVA ( if the Cos φ is different, please re-do the calculation )
So, 10 kVA if suitable with around 50% plus than the needed power, but certainly with the standard percentages of ” Drop Voltage “.
Regards.