jj said:
Hi Guys, I'm new here. Please help me out. I hv a 1 no. Exhaust Air Fan of 25kW with Full Load Current of 43.5A -400v. What is the required power/current rating should I supply? (i.e. isolator/socket outlet rating)
Can any of you guys out there, show me how can I calculate this and what is the formula?
Thanks.
Dear ;
If you want to install an Isolater or Socket, the nimonal current should be ” 63A “, But if you want to protect the fan's motor, it's better to use a ” Motor Circuit Breaker ” that should be adjusted around 43A.
Regards.