Home › Electrical Engineering Forum › General Discussion › power consumption of 1 ton a/c unit at 220 v?
- This topic has 5 replies, 3 voices, and was last updated 15 years, 4 months ago by
Ally Kanyondo.
- AuthorPosts
- 2011/02/13 at 5:19 pm #10387
admin
KeymasterHow much power will consume by a one ton a/c ? voltage 220 v single phase. And what will be the current if it is 2 phase?
2011/02/18 at 10:12 am #11833admin
Keymasteras per std. ton/ac unit at 220 v , it would take around 3.5 kw .
for 2 phase system , load kw will be come down .
why not u go for std. manufacturer catalog, where u will get all necessary inf. for each ton of ac unit .
thanks
2011/02/22 at 11:23 am #11835admin
Keymaster1 ton airconditioner ( 12000BTU/Hr) at 220volts 60 hz total line current rating between 6 to 8 amperes ( max for 1Ø and for 3Ø devide it with 1.73 ) it depend on ambient temperature the higher the temperature the higher the current, example 8Ax220V= 1760 watts
Regards,
HVAC consultant
2011/06/04 at 8:36 am #12137Hamdullah
ParticipantDear HVAC !
What comes the value 1.73 ? Here metioned ( max for 1Ø and for 3Ø devide it with 1.73 )
2011/07/26 at 5:04 am #12340admin
Keymastersajan joseph said:
How much power will consume by a one ton a/c ? voltage 220 v single phase. And what will be the current if it is 2 phase?
MAY I KNOW THE POWER CONSUMED BY 1TR,1.5TR N 2TR AC IN WATT/HR…………………..
2011/07/26 at 6:45 am #12353Ally Kanyondo
ParticipantHamdullah said:
Dear HVAC !
What comes the value 1.73 ? Here metioned ( max for 1Ø and for 3Ø devide it with 1.73 )
The value of 1.73 comes from the square root of 3. That means √3=1.73205