2011/02/05 at 3:46 pm #10376darkvaderParticipant
Dear colegues,
I’ve an electrical plant with a 6KV motor. The 6kv switchbreaker drawer has a multifunction relay including (51G) earth fault protection. The motor body is grounded to the earth protection electrodes system. The 6KV transformer that supply this motor is star configuration with the neutral point connected to a earth electode that is independent of the main ground earthing protection system where the motor body is connected. My question is the following:What value of regulation should i have in the multifuntion relay to prevent human indirect contact protection?
2011/02/25 at 7:10 am #11847adminKeymasterIndirect Contact protection limit is only 30mA as per standard code of practice.
2011/02/25 at 8:52 am #11850adminKeymasterNot possible.
2011/02/26 at 10:20 am #11853adminKeymasterHi. Anyone give me suggestion to start a project for my M.E. in industrial safety engineering in electrical sector. In the sense, i would like do it in Electrical safety. Tell me some ideas for electrical safety project. Must be capable of doing a semester. I've ideas, but like to know from professionals.
Mail me to azadcbe@gmail.com
9944574830
2011/03/01 at 10:22 pm #11864adminKeymasterA couple of thoughts that may help you.
By indirect contact I suspect you mean shock other than by direct contact with an active conductor. This form of shock will occur should somebody contact the motor earthed metal and true earth simultaneously with an earth fault occurring. The 51G relay will pick up the earth fault but not the indirect human contact. The danger comes when the fault current flowing raises the potential of the motor frame above true earth (EPR) and this then forces a current through a person in contact with the metal and true earth. The way to guard against this is to limit that EPR potential and/or the fault clearance time to levels regarded as non-injurious. Guidance on the allowable levels can be found in most HV standards. (Try AS2007 or IEEE80).
A second point is that you state that the transformer neutral and motor frame are connected to independent earth electrodes. This means that the fault path is via those electrodes and the earth. The electrode to earth connection can have a significant resistance and the higher this is the greater will be the generated step and touch potentials which effect the severity of indirect shock. Also, the higher it is, the lower the fault current will be and this may effect the clearance time of the relay. Unless there is a very good reason for having independent earths, I suggest that it would be better to equi-potentially bond the motor case with the transformer neutral grounding conductor, thus creating a low impedance path for the earth fault current which will minimise EPR and the clearance time. This could be done with the earth screen in the cable (if it has one) or a separate earthing conductor.
You could not practrically set 30ma at 20msec as a trip threshold on the 51G relay (It is an earth fault relay not an earth leakage relay) as there will be a small amount of leakage current in the motor to ground during starting. You would probably trip every time you tried to start the motor if you did select such a low threshold.
Hope that this helps.
-