megger test 3 phase transformer

Home Electrical Engineering Forum General Discussion megger test 3 phase transformer

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #10811
    doc70
    Participant

    I have a 13800V to 600V 2MVA step-down transformer.

    I need to megger test this unit, I have a megger good for 5KV and also a hi-pot DC tester (Megger brand).

    I am unclear of how to make the physical connections between the transformer and the testers.

    #12935
    pillay
    Participant

    @doc70 said:
    I have a 13800V to 600V 2MVA step-down transformer.

    I need to megger test this unit, I have a megger good for 5KV and also a hi-pot DC tester (Megger brand).

    I am unclear of how to make the physical connections between the transformer and the testers.

    make sure the transformer is not connected to any thing like the potential transformer,than carry out

    [1] usual insulation test between the frame and the connections terminations of the ht side.

    [2] test between frame and the lv side terminations.

    [3] test between ht terminations and LV terminations.

    [4] test between phases at HT side

    [5] test between phases at LV side.

    [6]

    #12947
    smithwalker
    Participant

    Hipot is an abbreviation for high potential. Traditionally, Hipot is a term given to a class of electrical safety testing instruments used to verify electrical insulation in finished appliances, cables or other wired assemblies, printed circuit boards, electric motors, and transformers.

    korg synth

    #12951
    Spir Georges GHALI
    Participant

    @pillay said:


    @doc70
    said:
    I have a 13800V to 600V 2MVA step-down transformer.

    I need to megger test this unit, I have a megger good for 5KV and also a hi-pot DC tester (Megger brand).

    I am unclear of how to make the physical connections between the transformer and the testers.

    make sure the transformer is not connected to any thing like the potential transformer,than carry out

    [1] usual insulation test between the frame and the connections terminations of the ht side.

    [2] test between frame and the lv side terminations.

    [3] test between ht terminations and LV terminations.

    [4] test between phases at HT side

    [5] test between phases at LV side.

    [6]

     

    Dear Doc70 ;

    Refer to Mr. Pillay said, I want to mentioned that the Insulation test Steps are mentioned by Mr. Pillay are 100% correct, but there’s 2 points :

    – If the primary voltage is ” 13.8kV “, the ” Insulation voltage ” should be around ” 17.5kV ” ( depending on the manufactere information ), so, what are the obtaining results with ” 5kV ” ?

    – If the secondary voltage is ” 600V “, the ” Insulation voltage ” should be around ” 800V ” ( depending on the manufactere information ), so, you can’t do the insulation test for the secondary with ” 5kV “.

Viewing 4 posts - 1 through 4 (of 4 total)