LED lights vs T5 and T8

Home Electrical Engineering Forum General Discussion LED lights vs T5 and T8

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #10178
    farah
    Participant

    i was assinged to conduct an experiment or calculate for these LED parameters such as whether it can save energy, power factor, illumination in lux, beam angle, optical efficiency, power consumtion, lifetime, harmonic distortion etc. can anyone help me to find the best method to test these parameters?thank you

    #11316
    Darragh Rogan
    Participant

    A quick way to do this would be to build a simulation room in Dialux, and light it first with the photometric data for T5 or T8 luminaries, and then LED.

    You would need to try to eliminate differences in the light fittings affecting your exercise to find differences in the light source – I would suggest using a similar light fitting that is adapted to use both T5 & LED – you should be able to find a batten type T5 no problem – and there are LED batten’s out there….

    The Dialux report will be able to predict circuit energy consumption, illumination (and uniformity of same), UGR for your beam angle but it won’t be able to help with lifetime, harmonic distortion, or one of the more noticeable differences between T5 & LED: light colour (kelvin) and Colour Rendering Index (and how linear the CRi line is…)

     

    Is this any help to you?

    #11317
    farah
    Participant

    Darragh Rogan said:

    A quick way to do this would be to build a simulation room in Dialux, and light it first with the photometric data for T5 or T8 luminaries, and then LED.

    You would need to try to eliminate differences in the light fittings affecting your exercise to find differences in the light source – I would suggest using a similar light fitting that is adapted to use both T5 & LED – you should be able to find a batten type T5 no problem – and there are LED batten’s out there….

    The Dialux report will be able to predict circuit energy consumption, illumination (and uniformity of same), UGR for your beam angle but it won’t be able to help with lifetime, harmonic distortion, or one of the more noticeable differences between T5 & LED: light colour (kelvin) and Colour Rendering Index (and how linear the CRi line is…)

     

    Is this any help to you?


     

    what is dialux?im a practical student major in power so i never learn anything about this before. and also what is UGR?

    #11318
    Laurent
    Participant

    farah said:


    what is dialux?
     


     

    As far as I know, Dialux is a free software and the reference for calculating lighting layouts : most lamps and luminaires manufacturers provide databases for this software. You can find more information and download Dialux software there

Viewing 4 posts - 1 through 4 (of 4 total)