- 2011/06/26 at 11:11 am #10528
Ally Kanyondo
ParticipantHi Guys
I need you help to solve the following problem.
“IAM ON THE FINAL STAGE IN DESIGNING ELECTRICAL INSTALLATION OF A 23 STOREY BUILDING BUT IM FACED WITH THE
FOLOWING PROBLEMS
1: THE AVARAGE LOAD IS APPROX 815kVA AND THE CLIENT WANTS TWO GENERATORS OF 500kVA BUT HE DOESN WANT SYCHRONIZATION
2: HOW TO LOCATE THE CENTRE OF THE LOAD IN THAT BUILDING i.e HOW TO CALCULATE CENTRE OF THE LOAD .
3: I NEED EXPLATION ABOUT DISTRIBUTION PILLAR AND RING MAIN UNIT AND AT WHAT PLACE DO THEY REQUIRED “
N.B I have decide to use BUS BAR RISER IN MY DESIGN
Any one with the help i wl be very glad to get your suggestations
Ally
United Rebublic of Tanzania
2011/06/28 at 5:17 am #12213admin
Keymasteryou know sir we need to synchronize the generators if you want to connect them in parallel or if your client doesnt want synchronization,the generator will supply loads differently.When it comes to center of load,well you have to know the ampacity of the whole circuits then you will know the correct size of wire and the necessary circuit breaker rating,,,… thank u
2011/06/28 at 1:11 pm #12228admin
Keymasteri think ther is no other way to combine this two generators except by synchronisation.
2011/06/28 at 2:29 pm #12229admin
KeymasterYOU CAN PROVIDE TWO SEPARATE LVSG WITH TWO ATS AS MAIN. BUT I PREFER TO HAVE SYNCRONIZATION WITH ONE SMALLER GENSET RATING. BUT ITS UP TO YOU WHICH IS CHEAPER. BUT THINK ABOUT THE EFFICIENCY OF THE SYSTEM
2011/07/08 at 9:43 pm #12295admin
Keymasteryou have to make the bulding two seprate parts every part take power from one geneator,
that means you connected 11 storey with one generator and ather 12 storey with another
2011/07/23 at 5:38 am #12346admin
Keymasterthe solutions are as follows
Divide the building load into two halves – supplly each halves with individual generator of 20% extra KVA and utiility service provider with ATS
Use Bus risers for very large buildings UPTO 20Floor and above.