HOW DO I CONNECT TWO GENSETS RATED 500kVA EACH WITHOUT SYCHRONIZATION TO SUPPLY ONE BUILDING

Home Electrical Engineering Forum General Discussion HOW DO I CONNECT TWO GENSETS RATED 500kVA EACH WITHOUT SYCHRONIZATION TO SUPPLY ONE BUILDING

Viewing 6 posts - 1 through 6 (of 6 total)
  • Author
    Posts
  • #10528
    Ally Kanyondo
    Participant

    Hi  Guys

    I need you help to solve the following problem.

     

    “IAM ON THE FINAL STAGE IN DESIGNING ELECTRICAL INSTALLATION OF A 23 STOREY BUILDING BUT IM FACED WITH THE

    FOLOWING PROBLEMS

    1: THE AVARAGE LOAD IS APPROX 815kVA AND THE CLIENT WANTS TWO GENERATORS OF 500kVA BUT HE DOESN WANT SYCHRONIZATION

    2: HOW TO LOCATE THE CENTRE OF THE LOAD IN THAT BUILDING i.e HOW TO CALCULATE CENTRE OF THE LOAD .

     

    3: I NEED EXPLATION ABOUT DISTRIBUTION PILLAR AND RING MAIN UNIT AND AT WHAT PLACE DO THEY REQUIRED “

     

    N.B I have decide to use BUS BAR RISER IN MY DESIGN

     

    Any one with the  help i wl be very glad to get your suggestations

     

    Ally

     

    United Rebublic of  Tanzania

    #12213
    admin
    Keymaster

    you know sir we need to synchronize the generators if you want to connect them in parallel or if your client doesnt want synchronization,the generator will supply loads differently.When it comes to center of load,well you have to know the ampacity of the whole circuits then you will know the correct size of wire and the necessary circuit breaker rating,,,… thank u

    #12228
    admin
    Keymaster

    i think ther is no other way to combine this two generators except by synchronisation.

    #12229
    admin
    Keymaster

    YOU CAN PROVIDE TWO SEPARATE LVSG WITH TWO ATS AS MAIN. BUT I PREFER TO HAVE SYNCRONIZATION WITH ONE SMALLER GENSET RATING. BUT ITS UP TO YOU WHICH IS CHEAPER. BUT THINK ABOUT THE EFFICIENCY OF THE SYSTEM

    #12295
    admin
    Keymaster

    you have to make the bulding two seprate parts every part take power from one geneator,

    that means you connected 11 storey with one generator and ather 12 storey with another

    #12346
    admin
    Keymaster

    the solutions are as follows

    Divide the building load into two halves – supplly each halves with individual generator of 20% extra KVA and utiility service provider with ATS

    Use Bus risers for very large buildings UPTO 20Floor and above.