How can the Transfrmers be Protected from Surge, Short Circuits, Lightning etc.

Home Electrical Engineering Forum General Discussion How can the Transfrmers be Protected from Surge, Short Circuits, Lightning etc.

Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #10554
    admin
    Keymaster

    Dear All,

    We have a a CaC2 manufacturing plant with an electric arc furnace. Incoming is 22kV which steps down to 11kV by an out door 22/11kV transformer, then goes to an old OCB, then to the indoor furnace transformer and finally to the electrodes. The furnace trandformer supplies 60-80 volts at 3000-5000 amps. We frequently faces transformer breakdown, especially during rainy season. We couldn't really make out what is happening each time, but we thought of various reasons such as those mentioned in the topic subject. Consultation with a number of electrical engineers could not yield a definitive reason nor a reliable preventive measure. One last and final proposal is to install an outdoor VCB before the 22/11kV transformer. Ofcourse, it is going to cost a lot and hence this request for advise. We have lightning arreastors in the system. If anybody can write a few lines, it is highly appreciated.

    Regards,

    Thomas

    #12349
    Ally Kanyondo
    Participant

    Dear Mr. Thomas

     

    Is the transformer breakdown appears more frequently during rain season only?.

     

    If ts so, try to check the cable terminations on both sides primary and secondary side.

     

    Somewhere water is leaking.

     

     

     

     

    Regards.

    #12356
    erickench
    Participant

    NEC 450.3 gives rules for sizing transformer overcurrent protection. There is a table in that article that gives the percentages for the overcurrent devices.

Viewing 3 posts - 1 through 3 (of 3 total)
  • You must be logged in to reply to this topic.