factory actual load calculation

Home Electrical Engineering Forum General Discussion factory actual load calculation

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #10375
    admin
    Keymaster

    Dear Sir,

     

    How can i check factory actual load in kva,

    according to electricity meter maximum demand load showing 375 kva. but in actual AMP in meter showing 1100 amps.

    now i want to add some more load.

     

    We have Capacity – 1000 kva

    Load AMP – 700 to 1100 AMPS showing on meter phase to phase

    i want to check how much – kva using..?

    #11805
    jones
    Participant

    Mohan , i think the 375 u r , talking abou the H.T side and amps 1100 u r talking about in the  L/T side. Anyway it can be solved by the basic  power P=VI cos of Phi formula. calculate it from one side , either HT or LT side find the amps and do the basic math. voltage u , know it , p.f u know it then find the p value and u can conver it by th  basic formula and convert it in KVA