- 2011/05/27 at 1:32 pm #10494
ANSARI
ParticipantI Have total load current 20amps in each phase i have 3phase cunnection i want to instal a generator so will u advise me what should be the capicty of generator.
2011/05/28 at 6:33 am #12112admin
KeymasterCapacity of the generator should be greater than total peak hour powerconsumption.
2011/05/30 at 6:17 pm #12116عبده همد
Participantwhen we connected agenerator with the network that must be the same as with 3phase event no that is not connected with
u must connected alone and I will put attension for this information to designe it with coming later thank u
2011/05/31 at 6:37 pm #12118admin
KeymasterThe capacity of generator must be the peak load current multiplied by its power factor and operating voltage then multiplied by square root of 3..The unit is watts.
2011/06/14 at 12:04 pm #12188Spir Georges GHALI
ParticipantANSARI said:
I Have total load current 20amps in each phase i have 3phase cunnection i want to instal a generator so will u advise me what should be the capicty of generator.
Dear Mr. ANSARI ;
to be able to calculate the Generator's power, we should know :
– Rhe Voltage's value between 2 phases.
once knowing, we apply the following formula :
S = 1.73 x U x I
where :
– S : generator's Power in ” VA “
– U : voltage between 2 phases
– I : line's current
but after calculation we should add at least 20-25 %, because the bigest effeicency for a generator done at 75-80% of his power.
Regards.