KeymasterThe incremental heat rate “the heat rate” is the ratio of inputfuel to the corresponding output powerFrom the incremental heat rate curve, the incremental fuelrate is deduced With F is the input fuel and P is the outputpower The reciprocal of the incremental fuel rate is known asthe incremental efficiencyTo operate at the maximum fuel efficiency, the point of the
minimum heat rate has to be definedMultiplying the incremental fuel rate by the fuel cost, theincremental fuel cost is obtained in ($/MWh)ExampleThe input fuel in (Btu/h) for a power plant with minimum and maximum power of 10 and 100 MW
respectively is given by:
F=(40+4*P + 0.012*P2)*106
where P is the generated power in (MW). Plot the input
output curve of the plant. Calculate the heat rate and plot itscurve against the output power.Assuming a fuel cost of 0.12*10-6 $/Btu, calculate
the incremental fuel cost in $/MWh and plot its
curve against the output power.
The fuel is given as:F=(40+4*P + 0.012*P2)*106
Also, the heat rate can be calculated from equation
input fuel (Btu/h)
output power (MW)
Heat rate = The fuel cost as a function of the output power is:
C=0.12*10-6 *F= 4.8 + 0.48*P + 0.0014*P2 ($/h)
The incremental fuel cost is:
Ifr = 0.48 + 0.0028*P ($/MWh)
2010/12/17 at 9:41 am #11683admin
Keymasterthe problem of economic dispatch is serous especially in scenarios where the demand is far greater that supply because you do not have any optionm,thus may resort to load shedding or peak power shaving.also from the concept of peak and base load power stations,this is no longer true in the above scenario to my understanding because you can not apply energy the economics because with the current set up of electrcity price regulatuion the criterion become unfeasible.