calculation regurding capacitor bank with reactor Home › Electrical Engineering Forum › General Discussion › calculation regurding capacitor bank with reactor This topic has 1 reply, 1 voice, and was last updated 12 years ago by Anonymous. Viewing 2 posts - 1 through 2 (of 2 total) Author Posts 2012/09/30 at 8:54 am #10912 AnonymousGuest Load 21.5 MW @ pf 0.85 to increase pf at 0.98 Question A) How many capacitor need ( MVAR) B) How many reactor need with respect capacitor ( Henry) NB. There are Induction furnace, Induction Motor are take power 2012/11/12 at 1:53 pm #13289 AnonymousGuest you need 9 MVAR and as i know to improve pf no need for reactor. Reactor used to improve the drop in voltage Author Posts Viewing 2 posts - 1 through 2 (of 2 total) You must be logged in to reply to this topic. Log In Username: Password: Keep me signed in Log In