3-pole or 4-pole contactor

Home Electrical Engineering Forum General Discussion 3-pole or 4-pole contactor

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #10479
    simone
    Participant

    Let's take the case that you have four one-phase circuits that you have to switch together. ¿Wich one of the following devices would you use?

    1) A four-pole contactor, connecting each pole to one of the four circuits

    2) A three-pole contactor, in order to switch the three phases, thus the four circuits downstream will be also switched

    #12079
    erickench
    Participant

    How can you have 4 single phase circuits? If it's a three phase circuit and your trying to setup an ATS you would need a four-pole contactor so that the neutral would also be switched. Otherwise the two power sources would not be separately derived.

    #12189
    Spir Georges GHALI
    Participant

    simone said:

    Let's take the case that you have four one-phase circuits that you have to switch together. ¿Wich one of the following devices would you use?

    1) A four-pole contactor, connecting each pole to one of the four circuits

    2) A three-pole contactor, in order to switch the three phases, thus the four circuits downstream will be also switched


    Dear Simone ;

     

    As I understood, you have ” 4 Single Circuits ” and you want to switch ” On & Off ” together, if yes, you should define if these 4 circuits will be supplied by ” 3 phases + neutral ” or ” 1 pahse + neutral ” .

    If the sypply is ” 1 phase + neutral “, you can choice a power contactor usning 2 of the main contacts to switch On & Off the supply, then the output of these 2 contacts will electrify the 4 circuits via ” 2 poles circuit breaker ” for each circuit. Noting the the nominal current of contactor should be equal or bigger than the total current value of these 4 circuits.

    If the supply is ” 3 phase + neutral “, you can choice a 4P power contactor usning the main contacts to switch On & Off the ” 3 phase + neutral supply “, then the output of this contactor will electrify the 4 circuits via ” 2 poles circuit breakers ” for each circuit. Noting the nominal current for contactor should be the current value for 2 circuits, because you have 2 circuits on the same phase.

     

    Regards.

    #12191
    simone
    Participant

    Thank you, Spir Georges GHALI,

     

    That's exactly what I needed to know. Perfect answer with a very clear explanation.

     

    Thanks and regards.

Viewing 4 posts - 1 through 4 (of 4 total)