Generator question

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #11039
    Anonymous
    Guest

    If generator is under-exited will the power factor be leading or lagging? Is this a desirable condition for the generator?

    Any feedback is appreciated. Thanks

    #13329
    Anonymous
    Guest

    The  power factor almost lagging.

    In most of the cases the exciter for the generator are use the inductive drives which has the lagging power factor ,since in addition the pf of the generator  becomes lagging.

    #13333
    Anonymous
    Guest

    Lagging power factor.

    #13343
    Anonymous
    Guest

    when generator is under exited i.e. it will absorb reactive power from the system i.e. it acts as an inductor so the power factor is lagging..