calculation regurding capacitor bank with reactor

Home Electrical Engineering Forum General Discussion calculation regurding capacitor bank with reactor

  • This topic has 1 reply, 1 voice, and was last updated 12 years ago by Anonymous.
Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #10912
    Anonymous
    Guest

    Load 21.5 MW @ pf 0.85 to increase pf at 0.98

    Question

    A) How many capacitor need (


    MVAR)

    B) How many reactor need with respect capacitor (


    Henry)

    NB. There are Induction furnace, Induction Motor are take power

    #13289
    Anonymous
    Guest

    you need 9 MVAR and as i know to improve pf no need for reactor.

    Reactor used to improve the drop in voltage 

Viewing 2 posts - 1 through 2 (of 2 total)
  • You must be logged in to reply to this topic.