Another way of looking at this, and the way it's measured during factory acceptance testing is:

 

Short circuit is placed on the LV connections, then simply apply a voltage to the HV connections to create Full Load current in the LV winding.

The percentage of HV voltage required to do this is also the percentage impedance.

 

example:

 

600V required on HV to circulate Full Load current in the LV.

 

If HV rated Voltage is 12000V

 

The %Z is 5%  or 600/12000

 

Hope this helps

 