Re: three phase power consuption calculations

Home Electrical Engineering Forum General Discussion three phase power consuption calculations Re: three phase power consuption calculations

#12096
admin
Keymaster

just ask the technical question dear …..its depends on the motor location from power source.but I think u want what size of cable required for this rating ….may be …so the current consumption for 100 kw motor is

100= 1.732x415x0.8x I

I =100000/1.732x415x0.8

I= 100000/575.024=173A