just ask the technical question dear …..its depends on the motor location from power source.but I think u want what size of cable required for this rating ….may be …so the current consumption for 100 kw motor is
100= 1.732x415x0.8x I
I =100000/1.732x415x0.8
I= 100000/575.024=173A