Re: the per unit system

#11385
admin
Keymaster

Hello,

 

I dont know any book to suggest, but i can give you a simple example.

In a per unit system the values are refered to some values taken as bases of the system.

For example if we have many transformers conected in an energy distribution  system, we can take

the values of one of them to make de bases of the per unit system :

 

 T1 ( we take this one)

 Sn=2500 kVA

 Un=15 kV

 

T2

 Sn=630 kVA

Un=15 kV

 

T3 

 Sn=500 kVA

 Un=15 kV

 

T……

 

Bases :

 Ub=U(t1)n = 15 kV

 Sb=S(t1)n = 2500 kVA

 Ib=2500*10^3 /(1,73*15*10^3) = 96,33 A

 

– Now lets make some calculations in per unit system

 

For example  we Have :

 

S(T2) = (630 *10^3) / (2500*10^3) = 0,252 pu

In(T2) = 0,252 / 1 = 0,252 pu    ( 1the denominator  is because we have Un(T2)=15 kV=Ub= 1 pu)

 

S(T3) = (500 *10^3) / (2500*10^3) = 0,2 pu

In(T2) = 0,2 / 1 = 0,2 pu 

 

So in pu :

 

Sn(T1) =1 pu  ,      Un(T1)= 1 pu ,  In(T1)= 1 pu

Sn(T2)=0,252 pu,  Un(T1)= 1 pu ,  In(T2)= 0,252 pu

Sn(T3)=0,2 pu,      Un(T1)= 1 pu ,  In(T3)= 0,2 pu

 

We can see very easily wich equipment is above or under our network reference, we dont need to do calculations with 

Ampere, Volt, VA, etc, it is also very usefull in some complex calculations.

 

If we want the real values we simple multiply the pu values by the bases :

 

Sn(T1) =1 * 2500 kVA       = 2500 kVA  ,    Un(T1)= 1 * 15 kV = 15 kV ,  In(T1)= 1 * 96,33 A        = 96,33 A

Sn(T2)=0,252 * 2500 kVA = 630 kVA,        Un(T1)= 1 * 15 kV = 15 kV ,  In(T2)= 0,252 * 96,33 A = 24,275 A

Sn(T3)=0,2 * 2500 kVA     = 500 kVA,        Un(T1)= 1 * 15 kV = 15 kV ,  In(T3)= 0,2 * 96,33 A     = 19,266 A