Re: short circuits on panel boards . how to prevent?

Home Electrical Engineering Forum General Discussion short circuits on panel boards . how to prevent? Re: short circuits on panel boards . how to prevent?

#12011
erickench
Participant

A short circuit occurs because an ungrounded conductor comes in contact with ground or neutal conductor or another ungrounded conductor such as a double line-to-ground fault. NEC 408.36 has rules for the protection of panelboards. They state:

a panelboard shall be protected by an overcurrent device having a rating not greater than that of the panelboard

 

If there is a fire or some other accident occurs then the panelboard is not protected properly. The main circuit breaker is supposed to trip whenever a short circuit or overload occurs. Perhaps the available short circuit current exceeds that of the AIC rating?