Re: Residual Current Circuit Breaker (RCCB)

Home › Electrical Engineering Forum › General Discussion › Residual Current Circuit Breaker (RCCB) › Re: Residual Current Circuit Breaker (RCCB)

#13470
Spir Georges GHALI
Participant

@milan vekariya said:
In any (2 OR 4 pole)rccb out put side neutral wire contact with earth, then rccb become trip(fault) neccesory. Remove neutral wire from earth contact. It is helthy (safe)condition.

Dear ;

The Neutral point in the output side of any RCCB or RCBO or ELCB shouldn’t be connected the the Earth point.