Re: power factors

#12180
Spir Georges GHALI
Participant

mehmood saleem said:

dear i want knowledge about power factors

our load is 500 ampare

and and current power factors is 0.8

i want pf 0.98

plz tell me this calculation i wated


Dear ;

 

To ba able to calculate the needed capacitors' power, we shoul know the voltage of the network.

Asune that's ” 400 V “, so, the calculation will be done as the following :

Q = P ( tg φ1   –    tg φ2 )

where :

     – P = 1.73 x 400 x 500 x 0.8 = 276800 W    or   276.8 kW

     – tg φ1 = 0.75      ( we found it  from Cos φ1 = 0.8 )

     – tg φ2 = 0.203    ( we found it  from Cos φ2 = 0.98 )

So :

Q = 276.8 ( 0.75  –  0.203 ) = 151.4 kVAR

That's the power of capacitors that you need, but it's better to install more by 10-15%

 

Regards.