Re: FINAL DISTRIBUTION BOARD (DB)

Home Electrical Engineering Forum General Discussion FINAL DISTRIBUTION BOARD (DB) Re: FINAL DISTRIBUTION BOARD (DB)

#12282
Spir Georges GHALI
Participant

Abhilash said:

DEAR SIR,
 

In this case we can go for 
 

 

 
 

Rated insulation voltage for the DB: Ui …… how much for doing Asta type test with this  DB as per IEC61439.
 

 
 

 
 


 

Dear ;
 

 

As we use ” Ui ” to do the tests for ” Dielectric , Clearance & Creepage “, and if the DB contains RCCB where for some of them ” Ui : 440V “, in this case we should use ” Ui : 440V ” to do these tests.
 

But :
 

– If there's ” MCB ( C60… & C120… )+ Vigi-block ” we can use ” Ui : 500V “.

– If there's ” MCB ( only NG125… )+ Vigi-block ” we can use ” Ui : 690V “.