Dear sir, each and every earthing is common for all uses but some term is consider.
PLC earthing is separated from electrical earthing please provide the copper earthing for PLC and GI for electrical.
electronic PLC Chassis should be isolated from body. and check continuity from electrical earthing to electronics earthing.
kindly note:
PLC earthing direct connection to electrode not in common grid or bus link.