Yes! Your interviewer was very correct! There is a very precise formula for sizing the earth strip:

 

S = I Root 't' / K

where, S is the cross sectional area of the earth strip, in sq.mm

I is the maximum anticipated earth fault current, in Amperes

t is the duration of the earth fault in seconds

K is a constant dependinng upon the material of the earth strip, type of insultaion & method of laying the earth strip (Pl. refer to IS 3043 for the values of these constants)