Supposing I have 3phase power installation, 80A/phase, with 420V/phase as well, what is the calculation for generator to be installed as standby?
Dear Puka :
This need a complete calculation but as a guide you must consider the followings :
1-KVA/KW: P=√3xVxIxcosφ =√3x420x80x0.8≈46000=46 KW , S=P/cosφ=58 KVA
2- as ISO3046 for standby load amount must be about 75% then you need 58/0.75 =77 KVA
3-above is valid only when you have resistive load if you have electromotor its related to :
– biggest motor
-starting to rated current ratio of it
-power factor of it
-permissible voltage deep(ΔU)
-direct on line or star-delta connection of it
-……
as a guide for starting of 1kw electromotor you need 3 to 5 kw og gen if ΔU=20%.
4-loading sequence:
e.g. if you have 2×15 kw motor and if you can start them one by one you need about 90 kw but if you want start them together you must have 150 kw gen.